http://www.pilotodyssey.com/PO/adm/images/imagemenu/smiley_cool.png PilotOdyssey.com Chat    http://www.pilotodyssey.com/PO/adm/images/imagemenu/find.png PilotOdyssey.com Google Search    http://www.pilotodyssey.com/PO/adm/images/imagemenu/emoticon_tongue.png FL400 Parts    http://www.pilotodyssey.com/PO/adm/images/imagemenu/emoticon_grin.png FL350 Parts    http://www.pilotodyssey.com/PO/adm/images/imagemenu/emoticon_evilgrin.png FL250 Parts    http://www.pilotodyssey.com/PO/adm/images/imagemenu/emoticon_unhappy.png Admin Email   
It is currently Thu Mar 28, 2024 9:44 am

All times are UTC - 5 hours [ DST ]




Post new topic Reply to topic  [ 12 posts ] 
Author Message
PostPosted: Tue Nov 22, 2016 11:02 pm 
Offline

Joined: Tue Jan 10, 2012 10:21 am
Posts: 2681
Location: NW Ohio / SE Michigan
So I recently (finally!) setup a my shop with its own dedicated heat source -- a ProCom 75k btu unit with thermostat. One of the last tasks was to install the LP conversion kit and then adjust the gas valve to 1.0-1.5" WC. Tool for the job is a manometer. Not exactly something i keep around, but also something simple to build out of some basic stuff lying around my shop. I used a piece of leftover 8020 extruded aluminum, some 5/16" clear tube, a hose barb with 1/8" thread, a piece of 1/2" ruled log paper, double sided tape, and some dyed water (food coloring). I couldn't find another one on the web with 8020, so thought I'd share. It also stores neatly on its side. =)

1st four pics are rotated (stupid phone).

-Dan A.


PS: AT THIS POINT, I HAD NO IDEA WHAT THE MANIFOLD PRESSURE SHOULD BE. UNDERSTAND I AM NOT A TRAINED HVAC PROFESSIONAL, LOL.


Attachments:
20161122_214218.jpg
20161122_214218.jpg [ 36.29 KiB | Viewed 1427 times ]
20161122_214226.jpg
20161122_214226.jpg [ 29.37 KiB | Viewed 1427 times ]
20161122_214231.jpg
20161122_214231.jpg [ 26.35 KiB | Viewed 1427 times ]
20161122_214235.jpg
20161122_214235.jpg [ 26.79 KiB | Viewed 1427 times ]
20161122_214300 (1).jpg
20161122_214300 (1).jpg [ 59.69 KiB | Viewed 1427 times ]
Top
 Profile E-mail  
 
PostPosted: Tue Nov 22, 2016 11:28 pm 
Offline

Joined: Tue Jan 17, 2012 3:19 am
Posts: 7698
Location: Hope, B.C Canada
DMoneyAllstar wrote:
So I recently (finally!) setup a my shop with its own dedicated heat source -- a ProCom 75k btu unit with thermostat. One of the last tasks was to install the LP conversion kit and then adjust the gas valve to 1.0-1.5" WC. Tool for the job is a manometer. Not exactly something i keep around, but also something simple to build out of some basic stuff lying around my shop. I used a piece of leftover 8020 extruded aluminum, some 5/16" clear tube, a hose barb with 1/8" thread, a piece of 1/2" ruled log paper, double sided tape, and some dyed water (food coloring). I couldn't find another one on the web with 8020, so thought I'd share. It also stores neatly on its side. =)

1st four pics are rotated (stupid phone).

-Dan A.


That's cool. How do you use it ??


Top
 Profile E-mail  
 
PostPosted: Tue Nov 22, 2016 11:55 pm 
Offline

Joined: Tue Jan 17, 2012 3:19 am
Posts: 7698
Location: Hope, B.C Canada
Never mind, I just looked it up lol.
http://www.rverscorner.com/manometer.html


Top
 Profile E-mail  
 
PostPosted: Sun Nov 27, 2016 6:19 pm 
Offline

Joined: Tue Jan 10, 2012 10:21 am
Posts: 2681
Location: NW Ohio / SE Michigan
Made a 2nd larger gage for the incoming LP pressure. Thought I had an issue but ended up just needing to bleed out the air more/longer out of the lines.

11" WC coming in from the regulator, and 2" WC flame adjustment on the gas valve (for efficiency and heat exchanger lifespan).

Good stuff!! Looking forward to some warm project space this winter. :-)



PS: if you came here from a Google search and don't yet own a buggy, check out this site and the For Sale section!


PSS: AT THIS POINT I WAS STILL TRYING TO DETERMINE THE CORRECT MANIFOLD PRESSURE FOR LP.


Attachments:
File comment: 11" WC gage
1.jpg
1.jpg [ 24.99 KiB | Viewed 1427 times ]
File comment: 6" WC gage in action
2.jpg
2.jpg [ 44.63 KiB | Viewed 1427 times ]
File comment: 75k BTU ProCom. Ceiling is slanted on a lean-to, so the heater is not "crooked".
3.jpg
3.jpg [ 24.61 KiB | Viewed 1427 times ]
Top
 Profile E-mail  
 
PostPosted: Sun Nov 27, 2016 8:39 pm 
Offline

Joined: Sun Jan 10, 2010 9:14 pm
Posts: 1779
Location: Ma
DMoneyAllstar wrote:
Made a 2nd larger gage for the incoming LP pressure. Thought I had an issue but ended up just needing to bleed out the air more/longer out of the lines.

11" WC coming in from the regulator, and 2" WC flame adjustment on the gas valve (for efficiency and heat exchanger lifespan).

Good stuff!! Looking forward to some warm project space this winter. :-)



PS: if you came here from a Google search and don't yet own a buggy, check out this site and the For Sale section!


Nice work, very nice shameless plug for the site. Well done.


Top
 Profile  
 
PostPosted: Sun Nov 27, 2016 9:57 pm 
Offline

Joined: Tue Jan 10, 2012 10:21 am
Posts: 2681
Location: NW Ohio / SE Michigan
Ha, thank you! I couldn't find crap for info on a shop heater install. It's like it's some kind of hocus pocus mojo magic or something (?). Turns out it's actually pretty effing simple!

Now if someone could go ahead and finish hanging the other 20 sheets of drywall for me. This was a winter project from...2 winters ago!


Top
 Profile E-mail  
 
PostPosted: Mon Nov 28, 2016 9:44 am 
Offline

Joined: Tue Jan 10, 2012 10:21 am
Posts: 2681
Location: NW Ohio / SE Michigan
My heater was making a high pitch whistle-sound at the flame and flame seamed pretty orange.

So in re-reading my gas conversion kit instructions, I believe I made an error. The recommended incoming gas pressure is 11-14" WC and then no more than a 2" WC DROP at the manifold (not 2" WC pressure). The target pressure at the manifold is 9.5" WC at my altitude in 0-3500'.

When I re-measured everything I'm consistently getting 11.5-12" WC line pressure and 9-9.5" WC at the manifold. No more whistle + she blows more heat.

Also the heater fan (not exhaust) never shuts off. I've got 4 connections on my tstat when I should only have 3, hence the extra connection is triggering the fan to run constantly. Need to get a roll of 3-wire tstat wire to mount the tstat where I want it (not hanging off the heater with stereo wire like in the pic) and then will have this thing purring on its own. Gonna be 50's-60's next few days, so no hurry.

Oh the joys of DIY!


Top
 Profile E-mail  
 
PostPosted: Wed Nov 30, 2016 1:19 pm 
Offline

Joined: Tue Jan 10, 2012 10:21 am
Posts: 2681
Location: NW Ohio / SE Michigan
Two more new issues to remedy:

#1) Regulator is freezing up. Either [A] the regulator isn't big enough (rated for max 75k btu, but my heater is a 75k btu), or [B] I need to tilt it down more so the vent will actually vent (it's horizontal now, but vent hole is on bottom and faces sideways and not down). I have another regulator rated up to 200k btu, but its an indoor type and therefore requires some plumbing changes. My once-worked-for-a-furnace-company-buddy tells me the bottles can freeze u if you use them on a day that was significantly warmer than the day the bottle was filled. Filled it when it was 34, and it was almost 60 out when I fired up the furnace a couple days later.

#2) Had almost a whole day of wind and rain which blew into the vent cap, down the vent duct, and created a small 6" wet spot on my barn floor. Not sure I can do anything about this one. Hoping it doesn't rain with 35mph gusts very often.


Top
 Profile E-mail  
 
PostPosted: Wed Nov 30, 2016 3:12 pm 
Offline

Joined: Mon Oct 25, 2004 10:02 am
Posts: 2865
Location: East Peoria IL
I believe you could vent it horizontally out the wall and slant it down so the rain would run out.


Top
 Profile E-mail  
 
PostPosted: Thu Dec 01, 2016 3:10 pm 
Offline

Joined: Tue Jan 10, 2012 10:21 am
Posts: 2681
Location: NW Ohio / SE Michigan
The horizontal vent kits cost as much as the dang heater, lol! :shock:

I'm replacing the vent elbow on the back of the heater with a tee that's got an aluminum cap on the bottom. It collect about 3-4 cups of water before it can run into the heater and onto the floor. And when it runs it'll burn off.

Also picked up an outdoor 2-stage 11" WC regulator with a huge vent port rated to 225k btu. No more freezing the regulator.

Another $50 of upgrades, but 100% necessary. That should about do it. :-)


Top
 Profile E-mail  
 
PostPosted: Tue Dec 06, 2016 9:50 am 
Offline

Joined: Tue Jan 10, 2012 10:21 am
Posts: 2681
Location: NW Ohio / SE Michigan
*DELETED*


Top
 Profile E-mail  
 
PostPosted: Mon Dec 19, 2016 7:32 pm 
Offline

Joined: Tue Jan 10, 2012 10:21 am
Posts: 2681
Location: NW Ohio / SE Michigan
The best advice I have for anyone installing the heater is to read the instructions, lol!

The LP supply pressure needs to be 11-14" WC.

The manifold pressure for my heater should be 8.5-9.5" WC. I'm getting between 8.5-8.8" WC.

ALSO...don't forget all of the parts in the NG-to-LP conversion kit. There should be a change made at the manifold as well as the burner orifices as part of the kit.

Spent all day in a 60'F shop while the high outside was 11'F. Unfortunately for this site, i was working on some built-ins for my house. Wife's priorities rule.


Top
 Profile E-mail  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 12 posts ] 

All times are UTC - 5 hours [ DST ]


Who is online

Registered users: Bing [Bot], Duneit, eseymour72, Google [Bot], Q, wyeeoddy


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Group